Installing a vapor barrier in the wrong location in a basement wall can end up trapping moisture in the wall assembly and supporting mold growth, leading to the rapid deterioration of the interior framed walls and finishes. It is better to not have a vapor barrier than it is to install one in the wrong place. In this video, we dive into the science behind vapor barriers in basements as well as some best practice strategies to provide interior moisture control without compromising the integrity of your home.
*Read the full article on basement vapor barriers here: * asiri-designs.com/resources-1...
150+ Free Building Science Articles : asiri-designs.com/resources-1
A Guide To Moisture Management For Residential Remodels (eBook) : asiri-designs.com/shop/ols/pr...
Request Building Science Consulting Services For Your Project: asiri-designs.com/consulting
------------------------------------------------------------------------------------
Music by: Bensound.com/royalty-free-music
License code: XPZ8XLOIR0NFWSEY

Пікірлер: 97

  • @RatedCfm-cz8ff
    @RatedCfm-cz8ff23 күн бұрын

    In western Canada, it was code for many years to have vapor barrier between the concrete wall & framing, as well under the drywall. The building code changed in the late 90s, no more vapor barrier permitted between the concrete wall,.& the framing. It was discovered that moisture was building up in between that vapor barrier, & the concrete, mostly from frost build up during winter months. The moisture would remain almost indefinitely, and emit a mildew odor, usually at its worst in the early spring.

  • @pwblackmore

    @pwblackmore

    23 күн бұрын

    There was a lot wrong with the BC building codes previously... 'leaky condos' being one prime reason for change. Water is the enemy of wood... do whatever you can to eliminate its ingress from outside first. Then make sure whatever is inside can breathe its way out.

  • @gnargnar1992
    @gnargnar199223 күн бұрын

    Probably the most underrated building engineering channel.

  • @stonecoldcustoms
    @stonecoldcustoms23 күн бұрын

    Great video - Amen! It took me 15+ years of home ownership before I learned this the hard way. Eventually figured out that no vapour barrier and rigid foam is the only way to go!

  • @timothychung4811

    @timothychung4811

    11 күн бұрын

    There is a reason why they're used in some aspects in concrete forming structures.

  • @theorenhobart

    @theorenhobart

    2 күн бұрын

    @@timothychung4811 oooh but it must be secret because you don't explain it ?

  • @larion3296
    @larion329624 күн бұрын

    Here in Sweden we are primarily installing permeable variants of basement insulation and drainage systems, such as Isodrän. They have probably been dominating for the last 15 years. The insulation is installed on the outside without any membrane. With gravel and drainage tubes below the basement walls. The idea is that the basement walls dry out from the inside, which requires a heated space, and causes a high humidity during the first months. With too high water table some membrane might be needed on the outside of the insulation.

  • @PonkyKong

    @PonkyKong

    13 күн бұрын

    They build a water proof concrete bottomed box.

  • @pwblackmore
    @pwblackmore23 күн бұрын

    Thankyou for this info - well-presented and informative. You are building for the future, not just to look good. I was working with a colleague when the Building Inspector approved the basement VB being to the local West Coast Canada code. When the BI left, my buddy cut the VB with a huge X, top to bottom - because, as he posited, the moisture would be retained within the stud bays... "Gotta let the walls breathe". I adopted that, but I really should have seen something like this video first. Remember, the code is the minimum... always improve on it. This video explains the best ways. I see you advise EPS, but it has its hazards - off-gassing, and combustibility in particular

  • @danielfortin5920
    @danielfortin59208 күн бұрын

    Insulation on the exterior wall. Simple and super effective ! The saturation point (dew point) won't be in the basement, but outside.

  • @rosegold7975
    @rosegold797524 күн бұрын

    Very informative. Was always unsure about building basement walls the best way

  • @camelface1
    @camelface125 күн бұрын

    Great uploads. Love the raw data.

  • @ASIRIDesigns

    @ASIRIDesigns

    25 күн бұрын

    Thanks so much, glad the videos have been helpful!

  • @bluearcherx
    @bluearcherx25 күн бұрын

    i assume this is for new builds with appropriate exterior water management and not for 84 year old basements

  • @ASIRIDesigns

    @ASIRIDesigns

    25 күн бұрын

    That's exactly right. To address older existing basements, check out this other video on the channel: kzread.info/dash/bejne/fqFt05qRYq-aZ6w.htmlfeature=shared

  • @jakesaari7652
    @jakesaari765223 күн бұрын

    Love all the graphics and clear information

  • @SnakeHandler-g7u
    @SnakeHandler-g7u25 күн бұрын

    Do you design residential buildings, or have a catalog I could look at purchasing plans from?

  • @jacobbeckstrand6764
    @jacobbeckstrand676425 күн бұрын

    Great info! I have the original blueprints for my 1960 built walk out basement house. I'll be doing a remodel in the next few years and suspect I'll reach out to you for the best way to go about insulating the remodel. I like the way you think. I live in Vancouver Washington and like that you are local

  • @SharpRealEstateGroup
    @SharpRealEstateGroup13 күн бұрын

    👍🏻👍🏻 thank you, very good info!

  • @kanento
    @kanento9 күн бұрын

    I have been thinking this for years as the basement walls would have moisture and you had the pink insulation it would get wet and not be able to breath with the vapor barrier. I found this was the case when I purchased another home build in 1950 with a reno in the basement. I noticed drywall was soft so I knew it was getting wet even with the barrier. I have to tear it all out and do foam board first

  • @multipotentialite
    @multipotentialite14 күн бұрын

    What do you recommend for a wood foundation with polyethylene which is not a perfect air barrier (overlapped and stapled instead of taped, gaps near receptacles, etc)?

  • @jdawes4403
    @jdawes440325 күн бұрын

    Thanks Sharif!

  • @rogiervantilburg3440
    @rogiervantilburg344012 күн бұрын

    Thanks for sharing!

  • @peterfroese8606
    @peterfroese86066 күн бұрын

    at 2:56 you talk about 'the right ratio' between the ridgid foam applied to the concrete wall vs the fiberous batts installed interior of that foam. I've read up on the ratios required for main floor walls, is this the similar ratio you are basis this off of, or is there a similar table where this can be looked up by climate zone? Thanks

  • @joecan
    @joecan6 күн бұрын

    Thinking back (24+ years ago), my builder used metal studs with pink insulation and vapour barrier from floor to ceiling in the whole basement. 7 years later, I finished the basement ( added some interior walls and electrical around the perimeter, so i had to cut the barrier to feed some electrical around the basement walls. I didn't notice any mold. This video makes though. Should I bust open a section to check, or just leave well enough alone?

  • @harrywood8196
    @harrywood81964 күн бұрын

    Ive been questioning this for many years. Concrete walls could sweat and therefore a plastic barrier would not let the insulated wall breathe behind the drywall

  • @dbdouglas
    @dbdouglas3 күн бұрын

    Put the framing a half inch or so away from the concrete walls. Put fiberglass insulation in, with paper-backing already on. Then stapled clear, plastic vapor-barrier to the framed walls - but only to the below grade height (of the outside dirt). 30 years & counting with zero problems.

  • @robertt9342

    @robertt9342

    3 күн бұрын

    Wouldn’t that create a tone of air and moisture penetration?

  • @dbdouglas

    @dbdouglas

    2 күн бұрын

    @@robertt9342 In the summer, we have a little de-humidifier on, like we did even before finishing the basement. No problems here, knocking on wood!

  • @smallcrush3
    @smallcrush313 күн бұрын

    I do have a vapor barrier in mine. But its applied right on the concrete wall, stops at about 2 ft from the floor. The studs are applied on the vapor barrier, which means the plastic film is squeezed between the studs and the concrete wall. There's also isolating foam panels which go from the ceiling to about 2ft from the floor. Dunno if that's desirable or not. No mold though, like at all, unless its deeply hidden behind the drywall... sure hope not!

  • @CommieCat
    @CommieCat18 күн бұрын

    This is quickly becoming ym favorite channel for building science. I hope you keep on keeping on. I like being an educated GC.

  • @NaturesInfiniteWELLth-fo6rs
    @NaturesInfiniteWELLth-fo6rs22 күн бұрын

    I recommend considering hemp fiber insulation alongside mineral wool…(one brand rockwool), with similar qualities/benefits. I am planning to build a hempcrete home and will use the hemp fibre bats in the ceiling and crawlspace. :)

  • @Langhorstiness

    @Langhorstiness

    14 күн бұрын

    hemp is organic and organic means it can turn into food for mold. All you need is some vapor condensation inside the hemp and you've just built a really expensive mold farm by accident. I don't think it sounds like the right application for hemp fiber insulation.

  • @johnwhite2576
    @johnwhite257624 күн бұрын

    I think you also need to do a video on exterior foundation insulation in this context….other than the issue of deterioration/bugs, it is another viable approach yes?

  • @ASIRIDesigns

    @ASIRIDesigns

    24 күн бұрын

    Absolutely, if you can protect the exterior insulation from bugs and moisture, it works great. The problem is that this can get complicated depending on what type of rigid insulation you're using. Rigid foams installed on the exterior of the foundation walls have to be treated like ICF foundations, with a fully adhered membrane bonded to the rigid foam, and even that can pose compatibility issues with the adhesives. Rockwool works but you need thick layers and a protection course. For durability reasons I very much prefer installing the insulation on the interior for below grade walls. You can also locate it interstitially, as in the case of a "sandwich" panel, and that works great as well since the insulation is protected.

  • @michaelriebandt6754
    @michaelriebandt67542 күн бұрын

    New Construction foundation concrete floor has visqueen (plastic sheeting) placed on floor before poring concrete and walls are of foundation have thick layer of more visqueen wrapped around outside walls sometimes repeating the steps. That is Building code (for decades) where I live also keeps moisture from entering past visqueen, Tar may not be enough.

  • @birdologytr3556
    @birdologytr35563 күн бұрын

    If you buy a new home save money on the initial purchase by leaving your basement undeveloped this will give you a chance to see what state your foundation walls are in by the end of construction.. seen some pretty large cracks in the past that just get covered up . If you have walls that are not in the mechanical room covered up and the rest are bare I would tear that out to make sure the builder wasn't trying to hide something... Just a friendly tip..

  • @elbuggo
    @elbuggo25 күн бұрын

    Even more better IMO would be to install Pordrän or Isodrän on the outside basement wall!

  • @paulstewart2444
    @paulstewart244413 күн бұрын

    Why does are building code here in Manitoba,Canada require it then???

  • @joeltaron1950

    @joeltaron1950

    11 күн бұрын

    Good question, I’m assuming many places have it as code. I’ve ripped out many basement walls in Winnipeg and found mold and rotten studs behind the poly. I think it has more to do with the quality of the foundation walls and damp proofing on the outside of the walls letting moisture in. Just my opinion on what I’ve seen in this area

  • @WalkerEnns
    @WalkerEnns24 күн бұрын

    How do you feel about insulated concrete forms? Based off the information in this video of having a couple inches of Styrofoam to prevent moisture/mold issues and still allowing the wall system to dry this seems like an ideal method of constructing not only basements but above ground as well.

  • @ASIRIDesigns

    @ASIRIDesigns

    24 күн бұрын

    ICFs are a good system but they aren't a panacea. As I was telling another person in the comments, ICFs absolutely must be protected from water infiltration and insect damage with a fully adhered membrane, but it gets complicated because the membrane and the adhesives have to be compatible with the EPS foam, otherwise things like solvent based adhesives dissolve the foam. Any system can be made to work as long as the the foundation is well drained and the layers are in the right location. That's the key.

  • @richpollock383
    @richpollock38323 күн бұрын

    Can you comment on using Zypex concrete waterproofing. I understand it promotes crystal growth into the concrete, sealing it, the product reacts to water infiltration.

  • @Langhorstiness

    @Langhorstiness

    14 күн бұрын

    Xypex is a liquid water crack sealer. It does not block transmission of air and/or water vapor. It would make no different for vapor moving through the concrete toward your vapor barrier.

  • @multipotentialite
    @multipotentialite14 күн бұрын

    Don't you also need to have an air barrier around the joists when you use rigid foam?

  • @greatitbroke
    @greatitbroke22 күн бұрын

    If its in the building code you have to install it to pass the building permit inspections. So whats your answer to that?

  • @daijoubu4529

    @daijoubu4529

    22 күн бұрын

    Rip it off after the inspector pass lol

  • @ASIRIDesigns

    @ASIRIDesigns

    22 күн бұрын

    You can use a smart vapor retarder instead of polyethylene to allow for drying if conditions get wet. It's allowed by code.

  • @theok4712
    @theok471211 күн бұрын

    There's technique for insulating basements with house wrap on the concrete block side first then studs, batt insulation and vapour barrier. What are you thoughts on this method?

  • @ASIRIDesigns

    @ASIRIDesigns

    11 күн бұрын

    It's the same problem.

  • @blehssed

    @blehssed

    11 күн бұрын

    @ASIRIDesigns disagree, it's not a problem on a properly poured and damproofed foundation wall

  • @theok4712

    @theok4712

    11 күн бұрын

    @blehssed how about a block wall built in the 1970's. It's probably not damproofed properly.

  • @WANDERER0070
    @WANDERER007021 күн бұрын

    Even better move is put Rigid foam board on the OUTSIDE basement walls ❤ all the way down to the frost line.

  • @pcatful
    @pcatful25 күн бұрын

    Did you say rigid foam IS a class II vapor retarder or rigid foam WITH a class II vapor retarder? 2:35.

  • @ASIRIDesigns

    @ASIRIDesigns

    25 күн бұрын

    Unfaced rigid foam itself IS a Class II vapor retarder

  • @kylejones4149
    @kylejones414911 күн бұрын

    Inspector in my area makes us valor barrier even with the foam board behind the framing

  • @Borisvanderoost
    @Borisvanderoost10 күн бұрын

    How about insulating it from the exterior side? Wouldn't that be simpler if it were a new build?

  • @francoisbouvier7861
    @francoisbouvier786115 күн бұрын

    Wo, wo. That one picture shows the back side of a shower/ tub situation. That's always a no no.

  • @frankrizzo2157
    @frankrizzo215714 күн бұрын

    my unfinished old basement was leaky damp dried out quickly

  • @lulutileguy
    @lulutileguy10 күн бұрын

    what about off gassing?

  • @vancegosselin
    @vancegosselin4 күн бұрын

    Mold food, yum

  • @MrFredscrap
    @MrFredscrap11 күн бұрын

    Couldnt you cast the basement wall with waterproof concrete mix (ie: materproof admixture)? that should address half of the problem with moisutre coming in from the outside.

  • @ASIRIDesigns

    @ASIRIDesigns

    10 күн бұрын

    You can, but here's the thing... All concrete cracks. Cracks are pathways for water to enter via hydrostatic pressure. So a drained system is the only way to prevent bulk water from getting inside. As for the other capillary forces and interior vapor drive/air leakage, they need to be addressed accordingly.

  • @jetterbenne2578
    @jetterbenne257812 күн бұрын

    Finished basements are not a good idea to begin with. There is this obsession of having a basement, finishing it and using it as a living space. it's just a ticking time bomb for disaster.

  • @adamford518

    @adamford518

    10 күн бұрын

    Not everyone has the luxury. Homes are expensive and space is limited so people have to make the best with what they have. Basements are common because the area is dug out for the foundation, so may as well make the best of unoptimal space.

  • @jetterbenne2578

    @jetterbenne2578

    10 күн бұрын

    @@adamford518 Sure it is cheaper but in most countries basements are for the pipes, storing wines, and roots.

  • @deletesoon70

    @deletesoon70

    9 күн бұрын

    Given this overheated real estate racket we are dealing with, maximizing utility and minimizing waste has been forced into people. For some reason.

  • @13Mappy

    @13Mappy

    6 күн бұрын

    Completely disagree.

  • @HuFlungDung2

    @HuFlungDung2

    6 күн бұрын

    I agree completely. A basement is just waiting for a flood event to happen, sooner or later. Naked concrete is easily washed up after a flood. A basement serves as easy access to the plumbing and heating systems,which inevitably fail and need repairs. That being said, my basement walls were styrofoam concrete forms, inside and out, so it can be heated when needed.

  • @sorenjensen3863
    @sorenjensen386310 сағат бұрын

    Or, do all foundations with icf

  • @jeil5676
    @jeil56768 күн бұрын

    I dont think I have any type of vapour barrier on my basement walls. Doesnt seem to have been a problem yet. house built in 60's.

  • @glennhiggs11
    @glennhiggs1121 күн бұрын

    HRV!!!!!

  • @evalangley3985
    @evalangley398512 күн бұрын

    I am right now searching how to limit radon getting inside my basement from the joint of my basement slab and basement walls. Those foam panels are unfortunately a chimney letting radon inside my basement. I don't know how to tackle the problem.

  • @ASIRIDesigns

    @ASIRIDesigns

    12 күн бұрын

    To address radon you need to do two things: Keep the radon out by ensuring that you're providing an adequate air barrier at the pressure boundary between the foundation and the conditioned space, and a means of radon removal, which is usually a passive or active subslab depressurization system. You don't want your home to be negatively pressurized, otherwise you're sucking soil gasses into the house. The house should be pressure balanced, or slightly positively pressurized in this case.

  • @hoildayfish5032
    @hoildayfish5032Күн бұрын

    I don’t do building or anything connected, cool vid but like why did i even watch it XD

  • @johnq2068
    @johnq206813 күн бұрын

    That’s what I did, all of it

  • @marklundeberg7006
    @marklundeberg700620 күн бұрын

    Why is soil at 100% humidity? Sounds like drainage issues.

  • @ASIRIDesigns

    @ASIRIDesigns

    20 күн бұрын

    Believe it or not, even "dry" soils are somewhat damp! You almost never have bone-dry soils except in extreme climates. Also consider that there is substantially less volume of air in soils, so the small amount of air that is inbetween the tiny gaps of soil particles aren't able to store much moisture in the first place.

  • @marklundeberg7006

    @marklundeberg7006

    20 күн бұрын

    @@ASIRIDesigns Interesting, yes reading around I see that even very slightly damp soil can have quite high humidity like 90+%.

  • @marklundeberg7006

    @marklundeberg7006

    18 күн бұрын

    ​@@ASIRIDesigns Ok I just stuck a hygrometer into a hole in the bottom of my foundation... I'm in a dry climate and I have no drainage issues, it's apparently bone dry crushed rock down there yet 98% humidity... Hah! The basement walls are insulated and barriered in the way you discourage. Unfortunately they are fully finished too... So I can't easily get the hygrometer into the walls.

  • @robertalkemade989
    @robertalkemade98910 күн бұрын

    ridgid foam

  • @ickster23
    @ickster2314 күн бұрын

    Avoid basements and crawl spaces of you can...

  • @frankrizzo5958
    @frankrizzo595813 күн бұрын

    Spray foam all the concrete in 2-3 inches of closed cell 2 pound foam and spray foam the rim joist areas as well

  • @elcrypto3623
    @elcrypto36236 күн бұрын

    House wrap with writing facing concrete,then framing,insulation and vapour barrier..standard practice in Canada.

  • @ASIRIDesigns

    @ASIRIDesigns

    6 күн бұрын

    @@elcrypto3623 This approach is wrong for the very reasons outlined in the video. Vapor barriers trap moisture in the framed cavity... Moisture can and will get inside, either from interior air leakage, inwardly driven vapor diffusing out of the concrete, or from bulk water leaks. That moisure must have the ability to dry out of the moisture sensitive framing.

  • @hotfudgemoney
    @hotfudgemoney25 күн бұрын

    Love this channel

  • @bwillan
    @bwillan22 күн бұрын

    If your foundation was built with ICFs you won't have this problem. I am surprised that ICFs are not more commonly used for foundations.

  • @Vertilgen
    @Vertilgen9 күн бұрын

    Video shows cold going straight through insulation to reach the vapor barrier. Just use better insulation!

  • @ASIRIDesigns

    @ASIRIDesigns

    9 күн бұрын

    "Cold" doesn't come inside, heat flow is from warm to cold. You need the benefits of an air barrier and vapor retarder in the insulation specs, or find another means of controlling condensation.

  • @blehssed
    @blehssed11 күн бұрын

    There's supposed to be an air barrier placed on the concrete prior to insulation. Arguably, the only time this may be correct would be when installing on freshly poured concrete.

  • @allantulli5546
    @allantulli554613 күн бұрын

    The proper approach is to seal the outside of the basement not the inside.

  • @rswow
    @rswow13 күн бұрын

    Seems like critical info. Please provide a version without the incessant music, else I'm driven away and missing out.

  • @acreguy3156

    @acreguy3156

    8 күн бұрын

    Agreed. So many YT video producers feel the need to add a background music track. It serves no purpose but to make the producer feel like a real Hollywood pro. The irony is, a REAL pros would NOT use music in such a video. Otherwise, great video!!

  • @joe-hp4nk
    @joe-hp4nk24 күн бұрын

    What did he say?

  • @durwardsaar6000
    @durwardsaar600013 күн бұрын

    I'd tell you to go back to trade school.

  • @artemirrlazaris7406
    @artemirrlazaris74069 күн бұрын

    Foam... flammable.... Pink insulation styrofoam... flammable... Fibreglass stillnumber one....