HOW TO WIRE PID FOR SINGLE OR MULTIPLE HEATING ELEMENTS | RE-EDITED & UPDATED

Тәжірибелік нұсқаулар және стиль

Hope this Update will help you all with your projects! It does make the difference!
*********************************************************
Thank you for Watching and Supporting my New Channel!
I am building by myself my own Workshop at home for Casting, Machining, and Pottery.
*********************************************************
Products Used in the Video:
1. 94% Alumina Dense Castable Refractory Cement
- Max. Service Temperature: 3270 F(1800 C)
amzn.to/3cr5sHF
2. TEMCo Kanthal A1 wire 18 Gauge 1 lb (253 ft):
amzn.to/30kdxIi
3. Multi-Function Belt Band Strap Quick-Release:
amzn.to/3qskrGf
4. Medium Duty Insulating Fire Brick (Aluminium Silicate Bricks):
amzn.to/3kSYcrN
5. PID Temperature Controller, MC701 Digital PID Temperature Controller:
amzn.to/30ngJTv
6. Heavy Duty Rocker Toggle Switch 20A 125V:
amzn.to/3rtu8p9
7. High-Temperature k-type Thermocouple Sensor 2372F/1300C:
amzn.to/3ekjywI
8. K Type Wire High-Temperature Fiberglass:
amzn.to/30n4kPv
9. 2000F Heat Spray Paint:
amzn.to/3cb8LT4
10: Foam Boards, 3/16" sheets (Many Sizes Available):
amzn.to/3ej7njT
11: TEMCo Kanthal A1 wire 16 Gauge 1 lb (159 ft) Resistance AWG A-1 ga:
amzn.to/3sXsXP0
12. Inkbird Solid State Relay 40DA DC SSR Black Heat Sink for PID Thermostat Temperature Controller
amzn.to/3rsJRES
13. Miniature Circuit Breaker 2 Pole 20A 400V
amzn.to/3cfEi6n
********************************************************
Camera and Lens I used:
1. Sony Alpha a6000 Mirrorless Digital Camera 24.3MP:
amzn.to/30nt0Ya
2. Meike 35mm F1.4 - Sony E Mount:
amzn.to/2ObmYr8
********************************************************
As they are Amazon Affiliate links with my Store ID: tncreation09-20 - It means if you purchase a product by click through one of those links, I will receive a small commission (at no additional cost to you). Therefore, please consider clicking through those links, this is a great way to support my work and my Channel.
Thank you very much W/ Warmest regards,
TN Creation.

Пікірлер: 141

  • @cullsans
    @cullsans3 жыл бұрын

    After watching 3 different 20 minute videos on wiring a PID controller, your video really connected all the dots and made it very clear for me, I appreciate you!

  • @poleline111
    @poleline1113 жыл бұрын

    As others have stated, nicely done - concise and to the point - very professionally created. Thanks for taking the time for us newcomers.

  • @play150
    @play1503 жыл бұрын

    This video is amazing. Like others, I spent such a long time trying to understand this with little success, but now I am ready to set up a PID controlled heater!

  • @allingerdoug
    @allingerdoug3 жыл бұрын

    Thank you for this straight-forward description of the steps to wire a PID to control a heating element. Before viewing this tutorial I had gone through literally hours of verbose blogs and videos but none presented such a simple diagram and explanation. Minutes after watching this I had my PID successfully controlling the heat in our burn off oven.

  • @Selamg1
    @Selamg1 Жыл бұрын

    Thank you for the lucid presentation on the PID connection. God bless ! From Addis Ababa, Ethiopia

  • @samueloneill1252
    @samueloneill12522 жыл бұрын

    This is exactly what I was looking for. Thanks for the video!!

  • @burakokumus6040
    @burakokumus60403 жыл бұрын

    Very nicely done! Thank you fo rthe time you spared to prepare this video. It's great.

  • @tableshaper4076
    @tableshaper40762 жыл бұрын

    Thanks so much, your effort is appreciated!

  • @NewsThatMatterUsa
    @NewsThatMatterUsa Жыл бұрын

    Thank you I had a slight understanding from other videos but yours helped me really understand I appreciate you

  • @ssranon
    @ssranon3 жыл бұрын

    thank you for a great video. very useful. looking forward to building my own composite curing oven soon.

  • @kretekfilter9687
    @kretekfilter96874 ай бұрын

    Thank you for making this video. Your knowledge sharing is really valuable.

  • @manveersingh5087
    @manveersingh5087 Жыл бұрын

    The way you explained things are very easy and clear at least learners don't have a hard time to understand, we appreciate your video, it's full of knowledge, keep it up brother

  • @MattPlaysRs
    @MattPlaysRs Жыл бұрын

    This video is awesome, I'm going to be converting a dial controlled kiln into a pid controlled kiln - really helped me understand what goes where, and WHY!

  • @TWFDeadzoneII
    @TWFDeadzoneII3 жыл бұрын

    Thanks for breaking it down so well.

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Thank you

  • @doriandervishi9189
    @doriandervishi9189 Жыл бұрын

    THX man, It Is so clear to understan, bye from Italy...

  • @user-oq9rx8rg3r
    @user-oq9rx8rg3r5 ай бұрын

    Hello, thanks for sharing your knowledge, i was searching exactly for pid controllers and thermocouples

  • @jasmac54
    @jasmac54 Жыл бұрын

    Very well explained bro....appreciate the afforts..

  • @heyyoubuddy6749
    @heyyoubuddy67499 ай бұрын

    Thanks this was very helpful, I will need to run 2 elements for my project.

  • @TimDonk
    @TimDonk2 жыл бұрын

    Finally. An explanation for the non electrician.

  • @AnhChinh
    @AnhChinh Жыл бұрын

    great job bro. helpful

  • @intelinside4226
    @intelinside42262 жыл бұрын

    This is great .... thanks

  • @updatename6637
    @updatename6637 Жыл бұрын

    The best explanation so far !!!!!

  • @ldmmmo9410
    @ldmmmo94103 жыл бұрын

    Amazingly clear and informative. Thank you !

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Hope this will help you in your projects !

  • @muhammadyaseen7719
    @muhammadyaseen77192 жыл бұрын

    Very amazing video, please make the electric convection oven video with three phase supply three heaters in series, and with fan forward and reverse.

  • @Ed-de3ro
    @Ed-de3ro2 жыл бұрын

    Hi, great video very easy to follow thank you for sharing. I have question can you add a fuse to this setup? 2nd can you add a count down clock as well.?

  • @wongedan9364
    @wongedan9364Ай бұрын

    thank you

  • @oldguyjourney
    @oldguyjourney3 жыл бұрын

    This video was outstanding! I was lost and this made my PID wiring so much less intimidating! Thank you SIR!!! Only question, and maybe silly, but what alarm is appropriate? Would you suggest a specific one? Again, thank you for this very clear and easy to follow video.

  • @Joshua-zq8ot
    @Joshua-zq8ot8 ай бұрын

    Great video, thank you. Where would a dry cut-off float switch fit in?

  • @1bigslug
    @1bigslug3 жыл бұрын

    Very informative. Thank you for the video!!

  • @PenumbralFigure
    @PenumbralFigure3 жыл бұрын

    Fantastic video! You made it very simple and clear. I successfully wired up my own PID circuit using it. I do want to add a way to cut power if a certain temp is reached, what would be the best way to do that? I was thinking wiring a normally closed relay in place of the alarm bell, with the other end connected to the positive/negative of the incoming plug. Is there a better way to do that?

  • @sufiyankp8153
    @sufiyankp8153 Жыл бұрын

    Thank you from india.... Very usefull bro thanks ആണ് loat

  • @user-ry1xi3ci1n
    @user-ry1xi3ci1n10 ай бұрын

    Thanks

  • @oranlemarindoran1872
    @oranlemarindoran18723 жыл бұрын

    thank you i like

  • @ChatchaiPummala
    @ChatchaiPummala3 жыл бұрын

    Very usefull information, thanks for your efforts, cheers!

  • @hanepbuhaytv8770
    @hanepbuhaytv87703 жыл бұрын

    new subscriber .. here.. from Philippines.

  • @TNCXBUNBOX

    @TNCXBUNBOX

    2 жыл бұрын

    Thank you!!

  • @mariusjenny8973
    @mariusjenny89732 жыл бұрын

    Great video ! You made it very clear and easy to understand. I just have two questions : I would like to power a 24V-90W cartridge heater, is a (max.) 10A 240V SSR enough /too much? I have found a PID controller that can provide a 3A 250V output , do i even need the SSR ? Thank you

  • @tbertw
    @tbertw2 жыл бұрын

    Love your video. I am in Texas, USA. Here we have 240 volts composed of two 120 volt circuits 120° out of phase. I am connecting the heating elements from an old Wall Oven. What mods are required of this circuit, if any? Thanks. Tim

  • @maciekkubiak8113
    @maciekkubiak81133 жыл бұрын

    thanks

  • @dirkhagar2399
    @dirkhagar2399 Жыл бұрын

    Great Video my friend. I have a 12v alarm busser so I assume I will need to power it by running a 12+ to pin 2 and pin 1 to red on the busser , then busser black wire to a 12v -black source.

  • @Alex-md8yj
    @Alex-md8yj3 жыл бұрын

    Great video. I do have a question. So i have dual elements on my strike water for homebrewing. I have one PID connected to one element and one connected straight to anotdd her outlet. If i parallel connect them is that drawing 240V or is it still drawing 120V? I also want to have them connected to one instead of 2 different powers.

  • @greatwhitenorth9159
    @greatwhitenorth91592 жыл бұрын

    Great video! This is exactly how I wired my curing oven up except, I only noticed after that I'd done this and it works, but I wired the input signal side of the ssr from the pid in series instead of parallel. After hooking up a multimeter im getting about 6v to each ssr instead of 12v but my ssr says 3v-32v DC so I being over 3v i don't think it cares whether it's 6v or 12v it sees the signal and completes the circuit on my hot leg to element. Am I totally off? Your opinion would be much appreciated, thanks!

  • @wernergraichen8193
    @wernergraichen8193 Жыл бұрын

    Excellent video but I want also to send the measured temperatures to excel in my notebook every 5 seconds. I suppose a small PLC with USB output (Raspberry Pi?) will be required but I am not sure about the configuration and recommended wiring. Do you have a video or suggestions about that? Many thanks

  • @AJH10000
    @AJH10000 Жыл бұрын

    Can that same wiring diagram be used on a powdercoating oven

  • @seanscimeca1
    @seanscimeca13 жыл бұрын

    Love your videos. The only thing I am not understanding is this, and everyone please comment to info - You are running 240v which means that there is no actual negative since both lines are hot. So how does the PID know which is hot and which is the negative in relation to getting power to it? You must be using a 3 wire 240V cable yes? two hot wires and one ground? this way you have one wire going to each the positive and the negative in the circuit breaker shown? Then it is a matter of just utilizing the one in the negative side of the circuit breaker to run to PID and split out to the heating elements right?

  • @cindywu4816
    @cindywu4816 Жыл бұрын

    This is the video I was looking for, I have a question, if you can receive it and give an answer: I have a 2500W heating element, can I connect to this temperature controller? Thank you.

  • @mrtechie6810
    @mrtechie6810 Жыл бұрын

    I want to add PID temperature control to my 240VAC instant hot water heater. What controller and sensor would you recommend? Is there such a thing as proportional heater control? A heater controller that factors in flow rate?

  • @bencoss7003
    @bencoss70032 жыл бұрын

    I understand that you're using this PID for your kilns, for temperature control, what I was wondering if you can use a PID for a furnace and room temperature, use it for a thermostat for your house?

  • @Mauldropper508.
    @Mauldropper508. Жыл бұрын

    The mc70q is in Celsius so do you know a comparable or same hook up for one that shows temps in Fahrenheit?🤔 Also if you needed let’s say 25+ amps one could swap out the on/of breaker switch to a higher value breaker since the relay is rated at 40amp correct? More concerned about a pid not in Celsius but one in Fahrenheit is needed any ideas on a pid for such?

  • @Ricardo_Wade
    @Ricardo_Wade2 жыл бұрын

    How accurate is this inkbird pid? The tempature read out on the pid is diffrent than what my infared thermo gun is reading pointing at the thermo couple

  • @carlosjimenez1333
    @carlosjimenez13333 жыл бұрын

    can i use this wiring for two contactors also , to control two heaters , ? can you upload a video for using two contactors , two heaters and one PID temperature controller , as shown in this video

  • @grillzbytroy8870
    @grillzbytroy88703 ай бұрын

    Will i need two ssr for multiple elements? I see 4 elements sticking out from behind my old panel

  • @TheAbbott1986
    @TheAbbott19863 жыл бұрын

    Do you need to use 2 ssr relays can I not power 2 elements in parallel via 1 ssr

  • @paullynch1938
    @paullynch19382 жыл бұрын

    How do you break in to the blue wire for example or do you mean you go from pin 8 to the element or am I just missing something, thank you

  • @Daniel-xx1dy
    @Daniel-xx1dy Жыл бұрын

    What if you only want 1 switch and 2 heating elements? Can you have two wires going to the - and + terminals of the SSR?

  • @matiasoliveramendez4056
    @matiasoliveramendez40565 ай бұрын

    Hola. Que tipo de controlador pid es? Gracias

  • @NewsThatMatterUsa
    @NewsThatMatterUsa Жыл бұрын

    With 240v tho there should be two hot leads from plug how do I wire this ? Plz help . Your video is super helpful but I am stuck on this .

  • @arlinaudrain7366
    @arlinaudrain7366 Жыл бұрын

    As per my above comment, aren’t 2elements connected to really act as one long element?

  • @eessence1179
    @eessence11793 жыл бұрын

    What's the time passed for heating element to reach desired heat value?

  • @chiuliechiu9760
    @chiuliechiu97602 жыл бұрын

    Sir wanna ask some help,, i was planning on building my self a curing oven for powder coating,, with 2 heating element, with 3000w each,, how much of an amps should i go with the specs??

  • @user-ym2fy1iq5e
    @user-ym2fy1iq5e2 жыл бұрын

    You are the first genius video i watch of this subject If i have 10 heating element do i need 10 ssr

  • @dirkhagar2399

    @dirkhagar2399

    Жыл бұрын

    I think it would depend on what the amp rating is of the SSR. You can't exceed that, add up the amps for each element to find out.

  • @finandagames4762
    @finandagames47622 жыл бұрын

    can you make an example of how to wire 2 PID rex c100 with 2 heating elements, mcb, switch on / off

  • @KracknCorn
    @KracknCorn3 жыл бұрын

    If you installed a limit switch, where would it go?

  • @rcistarliteinternational4502
    @rcistarliteinternational4502 Жыл бұрын

    Can you tell me the link to get the alarm bell

  • @dmctehnik4086
    @dmctehnik40867 ай бұрын

    Is it for multi heaters with more than 5, the diagram is the same???

  • @nate4029
    @nate40293 жыл бұрын

    Where does the ground wire connect to from the plug?

  • @davidlanday6102
    @davidlanday6102 Жыл бұрын

    Thanks for the video, what about the ground line? Do you simply splice the ground from the input power like directly to the ground of the element?

  • @davidlanday6102

    @davidlanday6102

    Жыл бұрын

    *Line

  • @samuelcalderon3807
    @samuelcalderon38073 жыл бұрын

    Thanks for answer me in the other video before this.. ok my friend if in my casé i have 4 heating elements equal.. each one gives 1500 watts.. and each one takes 7.5 amp because they are connected in parallel... i could use only 2 relay ssr 40 ampers each one.. and connected un parallel .. in other words 2 heating elements for one ssr? Could i do that.. and the switch on off.. these switch must be 20 amp at least.. because when they are connected they take 30 amp/2 = 15 amp each líne of 110 volts. . And i have house breaker fuse and a lot of protection just in case something happen? Thanks for your time and i will appreciate so much tour opinion. . Thanks

  • @samuelcalderon3807
    @samuelcalderon38073 жыл бұрын

    If i have 30 amps.. that take my heating elements and i am working witt 220 Volt. I must use a 220 volt switch .. or how much volts are in the ssr to the pid?..

  • @ChouinardPlaylist3
    @ChouinardPlaylist3 Жыл бұрын

    I would like to put 1 pid with 3 ssr for 3 element of 3000 watt (240v) each, can it be possible with only one pid? The switch on the ssr line doesn't need to be a big one(120v) they only cut one line, like you said, its only a switch for a contact NO on the ssr, the control will be done on the pid, right?

  • @arlinaudrain7366
    @arlinaudrain7366 Жыл бұрын

    Question: why is it necessary with two elements to use 2 SSR s. Rather than one 40 amp SSR?

  • @fouriejosh
    @fouriejosh2 жыл бұрын

    Possible to use two heating elements with a single SSR? 2x2kw heating elements, 1x40A SSR, 240VAC

  • @amrsafar9603
    @amrsafar96033 ай бұрын

    🥰

  • @RoyWanfried
    @RoyWanfried Жыл бұрын

    Hi, i buy an Rex-700 with 4-20mA Output to connect these Output to an Voltage Regulator SSR-40A with an 4-20mA Input. The Rex-C handle the SSR on and off, but not Power up and down like i hope. I cant find the function in settings. Can you help?

  • @bryansanders8477
    @bryansanders84773 жыл бұрын

    Good job on the video. Form Power to PID what Gauge is it?

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Thank you! For the PID - 14 to 16 Gauge should definitely be fine. I used 16.

  • @jerryblankenship9908
    @jerryblankenship99082 ай бұрын

    can you tell me what PID you are useing

  • @olliestobbs
    @olliestobbs3 жыл бұрын

    Great video. I just wondered how you would go about wiring multiple thermocouples in a larger oven. For example 3 elements + 3 thermocouples

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    For large scale, I've seen they use more than 1 pid for each thermocouple, they put all 3 pids to 1 big controlling box and set them with same setting (or different if needed). I think that make sense to me. But perhaps you can look for a pid with a special specification that has multiple thermocouple-lines in (about this I'm not so sure since I'm not professional and only do home DIY projects, but I think they exist.).

  • @USA__2023

    @USA__2023

    3 жыл бұрын

    Wow, hard to tell if this is a trick question. I work with PID controlled heating systems and when I read your question I had to laugh. I have not done anything like your scenario but I think it would be interesting to program 3 PIDs controlling 3 zones in the same area. I've seen heating controllers with multiple zones that do this but never had the need for them so haven't read how they work controlling one area or if they use PID tech.. I do know that you could connect all 3 thermocouples to one PID and have it control all 3 elements. In this case the PID would act on the average of the 3 thermocouples and of course the 3 elements would act as one unless you put a switch on each solid state relay like the poster of this vid did.. Another thing you could do if it works for you is put a switch on each solid state relay and each thermocouple. This would give you a few heating and or control options and shouldn't cause issues with the PID since it will just average any thermocouples that are connected, only concern would be the switch used for the thermocouple and it's connections.

  • @jake-hy2zb

    @jake-hy2zb

    Жыл бұрын

    I am doing the same. I had considered different solutions to running 3 or 4 elements but now after your great video I think I am going to run either 3 separate Pids or 2 combos! Thank you so much for all of your info here.

  • @alexborghi7101
    @alexborghi7101 Жыл бұрын

    second heat element the #11 goes to the positive of the second SWITCH, not relay, the graphic is correct but you must said it by mistake. great video

  • @shaknit
    @shaknit2 жыл бұрын

    Does anyone know of a pid controller that will vary the voltage output rather than just cycle on and off. Thanks

  • @abstecnoindustriac.a.2802
    @abstecnoindustriac.a.28022 жыл бұрын

    Can i Use two contactors , instead of two SSR , and get the same result , , 2 contactors for two heating elements , three contactors for three heating elements , and so on ?

  • @jiewsgarage
    @jiewsgarage9 ай бұрын

    How to add timer controler on this diagram?

  • @panjiutomo5253
    @panjiutomo5253 Жыл бұрын

    Sir i have question , how about the wiring diagram when using 8 heating ??

  • @samuelcalderon3807
    @samuelcalderon38073 жыл бұрын

    The difference between this configuration and the configuration before its just about the switch.. configuration before i has to use a switch bigger that support most amp. And in this configuration its just normal switch de amp.. or what else change in this configuration? And could i use a ssr of 40 amp.. to a heating elements conected uin parallel like tour pony one ssr to 4 elements heating?

  • @crobin2045
    @crobin20453 жыл бұрын

    Great new video, one question - from the circuit breaker to the PID and the heating element, the wire splits into two so what is the best way do that realistically, a wire connector?

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    You are definitely right. And since we are dealing with high temperature, especially from the heating element, Ceramic terminal blocks are great. Adding Aluminium Heatsink is great too, I used that in my builds.

  • @crobin2045

    @crobin2045

    3 жыл бұрын

    Thank you! One other thing... with the circuit breaker, exactly which type (not brand) because I’m having trouble finding one like that.

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    @@crobin2045 Sure, please check the Link below for the Circuit Breaker: Miniature Circuit Breaker 2 Pole 20A 400V amzn.to/3pvoO3g

  • @stetlerb

    @stetlerb

    3 жыл бұрын

    Xlnt video. Well explained. What PID controller do you recommend if I’m going to run to heating elements at 2000 W each. I would like to wire each one up separately so I have the ability to only run one if I choose. I would also need a light switch along with the alarm/buzzer that you show here. My application is for a double oven that I have converted into a single larger oven and I will be doing powder coating. My desired temperature is 400°. Thank you, any links to parts would greatly be appreciated. I need to build this by the end of this weekend.

  • @tonybaloney5606
    @tonybaloney56067 ай бұрын

    Is this for 240 volts??

  • @abstecnoindustriac.a.2802
    @abstecnoindustriac.a.28022 жыл бұрын

    I think ther is a mistake at the input of the SSR ( 24 a 380vac), is in short in this diagram

  • @Segerfabshack
    @Segerfabshack Жыл бұрын

    This is exactly what I need but I also want to add a timer . Do you have a video with a timer as well? Thanks!!

  • @dirkhagar2399

    @dirkhagar2399

    Жыл бұрын

    The timer is wired into the alarm. Either use alarm 1 or alarm 2 if it has two alarms. The alarms don't have any power to them so you will have to run a 110vac or 12vdc to one side of the alarm depending on what the timer can handle. Usually timers run on 12vdc

  • @ahzija9242
    @ahzija92423 жыл бұрын

    Great video, i just ask if it is the same principle in powder paint oven? Iam planning to make powder coating oven using household oven.

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    I would say yes. But please do more research and check carefully your project's requirements. Good luck on your project btw ! Cheers !

  • @ahzija9242

    @ahzija9242

    3 жыл бұрын

    Thanks TN for quick response. If you have enough time to make video, pls include 12volts fan for pid box controller, instead of alarm. Thank you again and happy new year.

  • @jameswiz
    @jameswiz3 жыл бұрын

    What is 12,13&14 used for

  • @jabainza8374
    @jabainza83742 жыл бұрын

    Is the Pids 220v?

  • @MAHER-ej9pi
    @MAHER-ej9pi3 жыл бұрын

    What of andele c900

  • @gl_kiwi1550
    @gl_kiwi1550 Жыл бұрын

    Each resistor bar uses 1 SSR, right (2 thermistor bars is to use 2 ssr)

  • @rcalin9354
    @rcalin93543 жыл бұрын

    Hi, nice work thanks for sharing. I am in the middle of making my own oven but i have a little problem. Instead of alarm when the oven reach the temp i would like a light. I put a light but nothing happen. Also i dont know the voltage i should put. I put a 220V light and didnt work. Should i put some 5V? Thanks

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Hi R Calin, the way you wire may vary, depends on the PiD model. But I would say, if it runs on 220v, then you light bulb should be 220v too, not 5v. Just check the diagram of you PID carefully, you might miss something. Good luck with your project Cheers!

  • @rcalin9354

    @rcalin9354

    3 жыл бұрын

    @@TNCXBUNBOX thank you. I will recheck it.

  • @rcalin9354

    @rcalin9354

    3 жыл бұрын

    @@TNCXBUNBOX i managed to make it work. Now everything it is ok but still have some questions. The wires to thermocouple and to heating element must be some special wires? Does them work with normal 2.5mm square wire? And also the ssr could melt isolation of wires inside the control box? I added a fan but not sure how much heat will be inside the control box. Thank you for your help and time to reply. Have a nice day!

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    @@rcalin9354 Hi Calin. For the Thermocouple -> Yes, It's definitely required a specific K or S-type wire (Depends on the thermocouple type). And for the Heating element, please use the fiberglass High-temperature wire (Ref link: amzn.to/3ahd7rL) - please check my Description for more details - You can find all of them on Amazon

  • @rcalin9354

    @rcalin9354

    3 жыл бұрын

    @@TNCXBUNBOX thank you for your help, i managed to make my own owen now. I give you credits for the electrical part. Here it is kzread.info/dash/bejne/jJaNzq6Op8q2mqw.html Thank you again!

  • @MarcelLui1
    @MarcelLui13 жыл бұрын

    Can I wire the heating elements in parallel? Or should I just separate them into multiple systems (buy multiple PID controllers) I need 4 heating elements total for my system.

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Hi Marcel, I would say multiple Pids is a safe choice, but that will bring the cost much higher, plus multiple Thermocouples are required, too. It really depends on how much power each of your heating element will draw, and do they have the same resistance value ? To my knowledge, parallel system works when you have same heating element resistance . Perhaps seeking for advices of a professional in this case is necessary, for safety and cost efficiency. Cheers,

  • @collegedays4924
    @collegedays49243 жыл бұрын

    I have a question, how does one measure how much amps the heating element is drawing?

  • @roweboatracing2606

    @roweboatracing2606

    Жыл бұрын

    You would have to use an amp clamp around the power wire. Or you could wire a dvom in series with one of the wires going to the heater.

  • @cedricjones6713
    @cedricjones6713 Жыл бұрын

    I followed the diagram but the coils arnt heating up

  • @stetlerb
    @stetlerb3 жыл бұрын

    Do you have a link for the high capacity plug ?

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Hi Stetler, please check out my Amazon link to see if this can help you, and have a look at their recommendations amzn.to/38kz8oZ For The PID, I found that people like this Inkbird model more: amzn.to/3bdi2v2 And my model is: MC701: amzn.to/34enDgj I also recommend you check out the "Soak/Ramp PID" - you will have so much more Options that you can do with it: amzn.to/3bcGvRd You are dealing with Two 2000W Heating elements so just pay attention to the SSRs, Heatsink, and ventilation(Cooling Fan). The good thing is that 400degree (I assume that is in Celcius) which is not high, so all the best to your project. I strongly believe you can make it! Cheers!

  • @mousumi7843
    @mousumi7843 Жыл бұрын

    How to Alam volt

  • @asafmammadov70
    @asafmammadov702 жыл бұрын

    👍🇦🇿

  • @jaihagusto272
    @jaihagusto2723 жыл бұрын

    Can u do this without the alarm?

  • @TNCXBUNBOX

    @TNCXBUNBOX

    3 жыл бұрын

    Yes you can ! Alarm is just optional.

  • @masumahmed7978
    @masumahmed79782 жыл бұрын

    HOW TO PROGRAM PLEASE Make a video

Келесі